Email: Password: Remember Me | Create Account (Free)

Back to Subject List

Old thread has been locked -- no new posts accepted in this thread
???
11/08/05 15:22
Read: times


 
#103421 - Supplier?
Responding to: ???'s previous message
Hi Steve,

Steve said:
Is there only one supplier in India ?


I reckon you are asking about the electricity provider to home(am I right?)

In India, the electricity board is run by respective state governments, adhering to common rules and policies formed by a Central Board.

There are private players, but not operating in every part of India. Tata and Reliance are names to quote in the private power sector.(Interesting to quote that during recent flood in Mumbai, Tata Power replaced damaged energy meters free of cost to its consumers)

Cheers,
Vignesh

List of 31 messages in thread
TopicAuthorDate
Diff between GND and Neutral.            01/01/70 00:00      
   Gnd and Neutral            01/01/70 00:00      
      UK Only            01/01/70 00:00      
         Depends            01/01/70 00:00      
   ground vs neutral            01/01/70 00:00      
      What happens if...            01/01/70 00:00      
         Safety ground is not for current            01/01/70 00:00      
            I recall            01/01/70 00:00      
            (Mal)Practices            01/01/70 00:00      
               death by electricity            01/01/70 00:00      
                  Neutral-gnd bond            01/01/70 00:00      
                     bonded in the panel, separate from there            01/01/70 00:00      
                        RE: bonded in the panel, separate...            01/01/70 00:00      
                     clause: IE rules            01/01/70 00:00      
                        IE ?            01/01/70 00:00      
                           Indian Electricity            01/01/70 00:00      
                              Only one ?            01/01/70 00:00      
                                 Supplier?            01/01/70 00:00      
   well 'gnd' is not necessarily groun            01/01/70 00:00      
      Summing up the points            01/01/70 00:00      
         you basically got everything wrong            01/01/70 00:00      
            to Mr. Suresh            01/01/70 00:00      
            Reversal...            01/01/70 00:00      
               correction            01/01/70 00:00      
   PHASE, NEUTRAL, SAFETY EARTH,...            01/01/70 00:00      
      Difference            01/01/70 00:00      
         Not in india as well            01/01/70 00:00      
            TN-S mains structure            01/01/70 00:00      
               Ours too            01/01/70 00:00      
                  I tried to explain this            01/01/70 00:00      
                     Hardly !            01/01/70 00:00      

Back to Subject List