#103399 - RE: bonded in the panel, separate...
Responding to: ???'s previous message
To elaborate, you only want to bond the neutral and ground at the service entrance. That means no bonding in subpanels, branch circuit infrastructure, or load-related equipment. Bonding at other places reduces the effectiveness of the safety ground, as it creates ground loops that enable current to flow on the safety ground. This increases the possibility that safety ground's potential will rise at the point of use (reducing its effectiveness of a safety measure), and also reduces the ground's value as a reference.

Why does this happen? It's a simple matter of current division. The old adage "electricity always follows the path of least resistance" is actually quite inaccurate. Think back to fundamentals of circuits. When you have a current that has a choice of two paths to follow (neutral and ground in this case), it does not simply choose the lower resistance path. It is true that more current flows through the lower resistance path, but a smaller amount still flows through the higher resistance path. It is a false assumption that either the safety ground or the neutral has 0 ohm resistance.

--Sasha Jevtic

List of 31 messages in thread
TopicAuthorDate
Diff between GND and Neutral.            01/01/70 00:00      
   Gnd and Neutral            01/01/70 00:00      
      UK Only            01/01/70 00:00      
         Depends            01/01/70 00:00      
   ground vs neutral            01/01/70 00:00      
      What happens if...            01/01/70 00:00      
         Safety ground is not for current            01/01/70 00:00      
            I recall            01/01/70 00:00      
            (Mal)Practices            01/01/70 00:00      
               death by electricity            01/01/70 00:00      
                  Neutral-gnd bond            01/01/70 00:00      
                     bonded in the panel, separate from there            01/01/70 00:00      
                        RE: bonded in the panel, separate...            01/01/70 00:00      
                     clause: IE rules            01/01/70 00:00      
                        IE ?            01/01/70 00:00      
                           Indian Electricity            01/01/70 00:00      
                              Only one ?            01/01/70 00:00      
                                 Supplier?            01/01/70 00:00      
   well 'gnd' is not necessarily groun            01/01/70 00:00      
      Summing up the points            01/01/70 00:00      
         you basically got everything wrong            01/01/70 00:00      
            to Mr. Suresh            01/01/70 00:00      
            Reversal...            01/01/70 00:00      
               correction            01/01/70 00:00      
   PHASE, NEUTRAL, SAFETY EARTH,...            01/01/70 00:00      
      Difference            01/01/70 00:00      
         Not in india as well            01/01/70 00:00      
            TN-S mains structure            01/01/70 00:00      
               Ours too            01/01/70 00:00      
                  I tried to explain this            01/01/70 00:00      
                     Hardly !            01/01/70 00:00      

Back to Subject List