First:
The equation I gave for power factor calculation does not calculate cos. Second: You can not divide a instant power value for an average apparent value. If the site time allows I wil prove the equation. V=v.sinwt I=I.sin(wt-teta) p=v.i=V.I.sinwt.sin(wt-teta) or p=V.I.sinwt[sinwt.cos(teta)-sin(teta).coswt] after simplify p=(V.I/2).[cos(teta)-cos(2wt).cos(teta)-sin(2wt).sin(teta)] After integrating for half a period cos(2wt) and sin(2wt) will be zero! So you will have the equation I gave. |