#190345 - Its the V and not the VA ?! Responding to: ???'s previous message |
Erik Malund said:
the rated voltage refer to isolation breakdown, so going up in amps will not have any effect. Thanks ...that put things in perspective. The way it was made out by the local technicians is that as long as you maintain the VA less than the rated, you are fine. As suggested, we go the screw terminal way and fit the socket once received. Raghu |